Discussion on lightning impulse test procedure Problematic: - A standard waveshape (1,2 µs ± 30% x 50 µs ± 20%) is specified. For most of the cases, there is no problem to meet this required waveshape with the actual test laboratory equipment; - For some transformers (large MVA and/or relatively low winding voltage and/or low leakage impedance), the tail time can not be obtained easily and for some cases, impossible to achieve even with the most powerful impulse generators ( 400 kJ). - The tail time achieved during the impulse tests is an important factor to demonstrate that the transformer is capable to withstand its rated BIL level; - The tail time is function of the capacitance used in the impulse generator together with the leakage impedance (for low leakage impedance); t2 (LTCG). To get the required waveshape, one of the options is to have the proper impulse generator capacitance or to use alternative methods as stated in IEEE C57.98. DE 1 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Problematic (continued): - IEEE C57.12.90, clause 10.3.1.1 does permit the use of a shorter waveshape provided that the impulse generator capacitance is equal to or greater than 0,011 µF; How short can be the waveshape to get a meaningful test (30 µs, 20 µs, 10 µs etc…)? - During previous meetings, it has been a general consensus that the capacitance value (0,011 µF) given in IEEE C57.12.90 is totally inadequate and shall be replaced by something else. - The concept of a "minimum impulse generator energy" has been proposed and discussed in several occasions since Leon (Mexico) meeting (November 1998). - Some manufacturers are equipped with more powerful impulse generators than others; DE 2 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Problematic (continued): - Two identical transformers made by two different manufacturers may be tested with different severities depending of the manufacturer laboratory capabilities. - This is not giving a fair market competition (manufacturer concern); - Some transformers may be not adequately tested (user concerns). - It is important to define minimum test equipment capabilities in order to have a common minimum testing severity within the transformer industry. DE 3 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Last meeting proposal: - We proposed to change the first paragraph of indent b) of clause 10.3.1.1 of C57.12.90 as follows: "The impedance of some windings may be so low that the desired time to the 50% voltage point on the tail of the wave can not be obtained with available test equipment. For such cases, shorter waves are acceptable provided that: 1- The optimum impulse generator connection is used (use of parallel stages, largest available capacitance); 2- The available energy from the impulse generator with the actual test connection and charging voltage is equal to or higher than the values given in the following table: DE 4 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Last meeting proposal (continued): Transformer category Single phase (kVA) Three phase (kVA) Minimum available impulse generator energy during tests1,2 (kJ) I II III IVa IVb 5 to 500 501 to 1667 1668 to 10000 10001 to 80000 80000 15 to 500 501 to 5000 5001 to 30000 30001 to 240000 240000 12,5 25,0 25,0 37,5 100,0 Notes: 1- Applicable only if the impulse tail time parameter ("t2") is outside the prescribed tolerances (50 s ± 20%). 2- Any generator configurations can be used during tests if the impulse waveshape "t 2" parameter is within the prescribed tolerances." DE 5 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Oklahoma City meeting decisions: 1- To revise the proposed minimum impulse generator energy values to cover not more than 80 % of the studied cases (actual values did cover from 83% to 92% of the studied cases). 2- Transformer categories to be aligned to the those defined in C57.12.00 for short-circuit performance (minimum nameplate rating i.e. ONAN where applicable). 3- An informative Annex has to be written explaining how the values were derived. DE 6 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Inputs received since Oklahoma City meeting: From Arthur Molden: 1- "As I believe we may have discussed during the last meeting, the value of inductance we are using in our calculations is based on the 60 Hz parameters of the transformer. If we were able to calculate the effective value of this inductance in the impulse frequency range I believe it would be a higher value. It would be quite easy to estimate the value of this inductance if we could observe the natural frequency obtained when a particular transformer was connected to a particular IG capacitor in an underdamped test circuit. Knowing the IG capacitance and the natural frequency we could easily calculate the effective inductance. And so for this reason I believe the value of IG energy we obtain from a calculation using the 60 Hz inductance value, is on the high side." Answer: By definition, the inductance is theoretically independent from frequency. Practically, due to other phenomena, the inductance can slightly increase at higher frequency. It is suggested to use the inductance value calculated from the power frequency leakage impedance as used by IEC 60076-4 for the calculation of the impulse generator components. This is giving impulse generator energy values slightly on the high side. DE 7 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Inputs received since Oklahoma City meeting (continued): From Arthur Molden (continued): 2- "This "over estimation" is compounded by two other parameters that are used in the calculations. 1) The use of the nominal value of tail time, 50 us. 2) The use of 80% efficiency for the IG voltage efficiency. If we were to use the minimum tail time of 40 us, the required IG energy would be reduced by a factor equal to (40/50)2. If we were to assume the IG efficiency was 100 %, the required IG energy would be reduced by a similar factor again (80/100)2. In other words our estimate of the required IG energy is using other estimated parameters, the values of which are all erring in the same direction. DE 8 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Inputs received since Oklahoma City meeting (continued): From Arthur Molden (continued): If we could obtain a better idea of how the 60 Hz based inductance value relates to the "effective" inductance during impulse testing, we could possibly determine our required energy with a little more precision. I believe the manufacturers would have a case for arguing that they only need to guarantee a 40 us tail. Also, I believe that the "optimistic" results that would be obtained by using a 100 % voltage efficiency in the calculations, would be somewhat offset by the fact that the inductance value we are using is based on a 60 Hz calculation. If there are a few occasions when these reduced energy requirements do result in a short tail, the manufacturer and customer can still elect to use "alternative means" of extending the tail." DE 9 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Inputs received since Oklahoma City meeting (continued): From Arthur Molden (continued): Answers: 1- We tend to agree that the calculated "minimum energy levels" should be based on a minimum tail time of 40 µs instead of 50 µs as calculated previously since the values are called "minimum energy levels". This will effectively reduce the values proposed during the Oklahoma City meeting (64% of the original proposal). 2- We did review several impulse test parameters used on our recent transformers orders and we have found that the impulse generator efficiency was generally ranging from 70% to 90%. Only few cases were outside that window. We found only few cases were the impulse generator efficiency was as low as 50% and for few other cases, the efficiency was close to 100%. The original hypothesis using a generator efficiency of 80% was not so pessimistic. We do recommend to continue to use a mean value of 80%. DE 10 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Inputs received since Oklahoma City meeting (continued): From Loren Wagenaar: 1- "I plotted the minimum generator energy (MGE) vs. MVA and BIL rating of the winding. The result is that for a given BIL, MGE is linear with MVA. The significance of this fact is that we can, if we wish to, specify a minimum MGE at a given MVA (e.g., 100 MVA) for a given BIL and then ratio accordingly for the particular MVA of interest." Answer: Yes, the MGE is linear with the MVA and inversely proportional to the leakage impedance. By using your suggestion, we did derive a formula giving the minimum impulse generator energy as a function of tail time, BIL, power rating, winding voltage and leakage impedance (see the revised proposal). This formula gives only the minimum impulse generator energy level for a particular transformer design which can be lower or higher than the values proposed originally. If lower, every body (manufacturers and users) will be happy because you do not need a so powerful impulse generator and the required waveshape tail time will be achieved. On the other hand, if the number computed is higher than the limits proposed, you need an impulse generator having an higher capacity. For some cases, even the most powerful impulse generators ( 400 kJ) will not be able to produce the required waveshape. Thus, we need to propose a certain upper limit for which manufacturers can design their test plants. DE 11 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Inputs received since Oklahoma City meeting (continued): From Loren Wagenaar (continued): 2- "I added a couple of BIL levels (200 and 250 kV) at the bottom end of the range. These correspond to 34.5 and 46 kV system voltage, respectively. These were added because AEP often has tertiary windings with 34.5 kV and 200 kV BIL ratings." Answer: Of course, these cases have to be covered and to my opinion implicitly covered in the proposal. We have computed (by using the formula) some of our actual cases and it appears that the required energy level to obtain a tail time of 40 µs is generally huge and generally exceed the values proposed. Moreover, in a lot a cases, no manufacturers have the capability to test them with an appropriate waveshape without the use of a resistor added on the other terminals. For our large auto-transformers with tertiary winding, they normally fall into "Category IVb". DE 12 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Inputs received since Oklahoma City meeting (continued): From Loren Wagenaar (continued): 3- "The standard allows for a minimum time to half value of 40 us. I have therefore added a spreadsheet for 8 % impedance for 40 us and compared it with the MGE values at 50 us. The result is that the MGE's for the 40 us waveshape are about 64 % of those for 50 us. This method of defining the MGE seems more straight forward to me, rather than to define an arbitrary percentage of cases where the MGE can be met. It is preferable to have something that already falls within standards, and the 40 us (50 us minus 20 % tolerance) does." Answer: See Art's comment no. 2. Calculation have been revised using a minimum tail time of 40 µs. DE 13 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure New calculations: New sets of calculations have been performed by using the following assumptions: The common input data used for calculations were: - single phase, two windings transformers; - system voltages and impulse levels taken from IEEE C57.12.00; - generator efficiency: 80% (practical value); - time to 50%: 40 s (minimum tail to be met); - minimum impulse generator capacitance calculated by using equation A.8 of IEC 60076-4. A total of 1044 cases were computed. DE 14 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure New calculations (continued): Studied cases Transformer Range of power category (minimum nameplate rating, single phase ONAN) I II III IVa IVb DE (kVA) 5 to 500 (5, 10, 20, 40, 80, 160, 320 and 500) 501 to 1667 (501, 1000 and 1667) 1668 to 10000 (1668, 3200, 6400 and 10000) 10001 to 80000 (10001, 20000, 40000 and 80000) 80001 to 600000 (80001, 160000, 320000 and 600000) Range of rated system voltage Range of leakage impedance (kV) 1,2 to 69 (1,2, 2,5, 5,0 8,7,15,0, 25,0, 34,5, 46,0 and 69,0) 1,2 to 69 (1,2, 2,5, 5,0 8,7,15,0, 25,0, 34,5, 46,0 and 69,0) 8,7 to 230 (8,7, 15,0, 25,0, 34,5, 46,0, 69,0, 115, 138, 161 and 230) 69 to 765 (69,0, 115, 138, 161, 230, 345, 500 and 765) 69 to 765 (69,0, 115, 138, 161, 230, 345, 500 and 765) (%) 1,0 to 4,0 (1,0, 2,0, 3,0 and 4,0) 15 Number of cases studied 288 3,0 to 6,0 (3,0, 4,0, 5,0 and 6,0) 108 4,0 to 8,0 (4,0, 5,0, 6,0, 7,0 and 8,0) 200 8,0 to 14,0 (8,0, 9,0, 10,0, 11,0, 12,0, 13,0 and 14,0) 8,0 to 14,0 (8,0, 9,0, 10,0, 11,0, 12,0, 13,0 and 14,0) 224 224 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure New calculations (continued): - The proposed energy levels were chosen in order to cover 70%, 80% and 90% of the cases studied (80% has been agreed upon during the Oklahoma City meeting); - A maximum of 100 kJ has been used because this is the upper limit that can be obtained from today's impulse generator; - Transformer power ratings have been categorized according to the classification used in C57.12.00 for short-circuit withstand capability (minimum nameplate rating; ONAN; as agreed during the Oklahoma City meeting); . Existing category IV has been split in two (IVa and IVb) because this range is too large for testing circuit requirements. DE 16 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure New calculations (continued): Studied cases Transformer category Range of power Minimum available impulse generator energy during tests to obtain a tail time of (minimum 40 µs nameplate rating, single phase ONAN) (kVA) Covering 90% of the studied cases I II III IVa IVb 5 to 500 501 to 1667 1668 to 10000 10001 to 80000 80001 to 600000 (kJ) Covering 80% of Covering 70% of the studied cases the studied cases 7,0 30,0 21,0 30,5 See note 3,0 15,0 13,5 22,0 See note 1,6 8,0 9,5 16,5 See note Original proposal based on a tail time of 50 µs 12,5 25,0 25,0 37,5 100,0 Note: For a minimum limit of: 100 kJ, 61% of the studied cases will be covered 75 kJ, 51% of the studied cases will be covered 50 kJ, 35% of the studied cases will be covered DE 17 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure New calculations (continued): Observations from the results obtained: 1- The new values are: - 24% of the original value for Category I transformers; - 60% of the original value for Category II transformers; - 54% of the original value for Category III transformers; - 59% of the original value for Category IVa transformers. The reduction for Categories II to IVa is mainly due to the change from a tail time of 50 µs to 40 µs while the reduction for Category I is also due to the fact of covering only 80% of the studied cases instead of 90%. 2- The fact of using a "t2" time of 40 µs instead of 50 µs reduces the required energy by 32%. 3- The extra impulse generator energy required to cover the last 10% (i.e. from 80% to 90% of studied cases) is quite significant. Numbers are approximately doubled. DE 18 Pierre Riffon P. Eng. 03/03/06 4- A value of 100kJ for Category IVb seems to be still valid because only 61% of the studied cases are covered. DE 19 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Modified proposal: - We propose to change the first paragraph of indent b) of clause 10.3.1.1 of C57.12.90 as follows: "The impedance of some windings may be so low that the desired time to the 50% voltage point on the tail of the wave can not be obtained with available test equipment. For such cases, shorter waves are acceptable provided that: 1- The optimum impulse generator connection is used (use of parallel stages, largest available capacitance); 2- The available energy from the impulse generator with the actual test connection and charging voltage is equal to or higher than the values given in the following table: DE 20 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Proposal (continued): Transformer category Single phase (kVA) Three phase (kVA) Minimum available impulse generator energy during tests1,2,3 (kJ) I II III IVa IVb 5 to 500 501 to 1667 1668 to 10000 10001 to 80000 80000 15 to 1500 1501 to 5000 5001 to 30000 30001 to 240000 240000 3,0 15,0 15,0 25,0 100,0 1- Applicable only if the impulse tail time parameter ("t2") is outside the prescribed minimum tolerance (40 s). 2- Any generator configurations (available energy) can be used during tests if the impulse waveshape "t 2" parameter is within the prescribed tolerances. 3- For windings rated below 95 kV BIL, a minimum impulse generator capacitance value of 4,0 F may be used instead of the minimum energy level given in the table. This minimum capacitance value may be used in conjunction with the alternative methods described in IEEE C57.98. DE 21 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Modified proposal (continued): The minimum impulse generator energy required to meet the minimum tail time (40 µs) during an impulse test on a particular transformer design and connection can be estimated by using the following equation: 2 f t2 U BIL VA 2 z U 2 Emin . 2 where: Emin.: minimum energy required from the impulse generator (joules); f: power frequency, 60Hz; t2: tail time (second); t2 equal 40 µs; z: impedance in p.u. seen from the impulsed terminal; U: winding rated voltage (volts, phase-to-phase); UBIL: rated BIL of the tested winding (volts); : impulse generator efficiency in p.u.; = 0,8; VA: three-phase power rating in volt-ampere for which the impedance "z" is defined. DE 22 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Modified proposal (continued): 200 250 350 450 550 125 650 100 750 1050 75 1550 50 2050 25 200 0 250 8 9 10 11 12 13 14 350 450 Impedance, % 550 Figure YYY: Example showing the variation of minimum generator energy for a 100 MVA as a function of 650 Minimum Generator kJ Generator Capacity as a Function of Impedance & BIL to Obtain 40 us Tail on a 100 MVA 1-Phase Transformer BIL and impedance value. DE 23 Pierre Riffon P. Eng. 03/03/06 Discussion on lightning impulse test procedure Modified proposal (continued): If the calculated impulse generator energy for a particular connection is such that the minimum time to 50% (e.g.: 40 µs) can not be achieved, the manufacturer shall mention it during the bidding stage. The manufacturer shall also state the strategy that will be taken to obtain an acceptable waveshape. For cases where the minimum tail time (40 µs) can not be achieved, even by using the minimum energy level given in the previous table, resistors can be added on the non tested terminals as described in clause 10.3.2.1." DE 24 Pierre Riffon P. Eng. 03/03/06